Enforcement Notice

Date of notice:
26/10/2020
Required compliance:
15/02/2021
Notice served to:
Landside Property Management Limited
Property type:
Purpose Built Flats>=4 floors
Applies to:
Eros House, Brownhill Road, London, SE6 2EF
Served to:
2a Victoria Road, The Curve, London, NW4 2AF

Additional Information

Borough premises situated in: Lewisham

Responsibility of person on whom notice served: Other person having control

Applicable legislation: Article 30: Regulatory Reform (Fire Safety) Order 2005

Comments

  • The time allowed for completion of remedial works has been extended to 12 August 2021

    27/04/2021

  • Extension of time issued new required works completion date changed to 12th April 2021

    09/02/2021

Articles

  • Article 8

    Failure to provide adequate fire separation between floors only.

    Provide adequate fire separation.

  • Article 9

    Failure to review the fire risk assessment.

    Implement regular program to review fire risk assessment.

  • Article 11

    Failure in the effective management of the preventive and protective measures.

    Implement arrangement for the effective planning, organisation, control, monitoring and review of the preventive and protective measures.

  • Article 13 Fire Warning

    Failure to provide a suitable method of giving warning in case of fire.

    Provide a suitable method of giving warning in case of fire.

  • Article 14

    Failure to provide and/or maintain adequate and clearly indicated emergency routes and exits that lead to a place of safety.

    Ensure that adequate escape routes and exits leading to a place of safety are provided and that these are maintained clear and available for use at all times that the premises is occupied.

  • Article 17

    Failure to ensure that the premises and any facilities, equipment and devices are maintained in an efficient state, in effective working order and in good repair.

    Ensure that adequate maintenance systems are in place to ensure that the premises and any facilities, equipment and devices are maintained in an efficient state, in effective working order and in good repair.

  • Article 18

    Failure to appoint sufficient competent persons to assist in undertaking preventive and protective measures.

    Appoint sufficient competent persons to assist in undertaking preventive and protective measures.